Hi,
Your pics and video do help. Your sequence for trying to light the pilot is not entirely correct. In your video, you are doing the steps too quickly.
Here are photos of the furnace with the wiring diagram.
Also here's a video of it running and me attempting to light it.
Could low propane levels be the reason for it not lighting? Someone said if it isn't level that can cause it not to light.
Video is here
https://photos.app.goo.gl/9Y7KFTfPRPHMvjPT8
Here is a user manual for that furnace. See page 5 for the pilot lighting instructions.
https://www.sunlineclub.com/forums/downloads.php?do=file&id=5652
You had the blower running, which is good, as the T stat was turned up high enough to call for heat.
Yes, you turn the red knob to pilot, and you did, then you pressed the ignitor a few times. But I did not see you do the rest of the sequence correctly here.
Ideally, you use two hands to do this, and I understand that to do the video, you had to hold the phone.
Here is what I did not see you doing.
With one hand, and in the pilot position, hold the red knob in, and keep it holding it in. Then push and snap the igniter several times. AND, you have to hold the knob in for at least a minute as the directions on page 5 state. If you let off the red knob too soon, the whole sequence has to start over.
I'll explain what is happening so you can better understand it. The gas valve pilot system has a thermocouple flame-sensing feedback system. This is part of the safety system, so if the pilot ever blows out, it shuts down the gas system. The thermocouple with its copper tube is a feedback system that uses heat to create a small voltage when heated at the sensor's tip.
When you hold the red knob in, a small amount of gas flows to the pilot nozzle/orifice. At this point, gas will only flow when the knob is pressed in. You hit the igniter a few times, which is supposed to light the pilot flame. Once the flame is lit, the flame heat heats the thermocouple tip and sends a signal back to the gas pilot valve that it is OK to keep the pilot flame lit. That signal takes time for the thermocouple to expand from the heat and hold the pilot flame open. If you let go of the red knob too soon, the pilot flame goes out and will never hold the pilot valve open and you have to start all over. If the flame blows out once lit, the thermocouple will sense lack of flame and shut off the pilot as a safety.
The above is what is supposed to happen. In your case, you do not know if the gas flows to the pilot, if the igniter sparks, or if the flame is lit. If the flame does light, does the thermocouple and the gas pilot valve work properly?
So, if you are doing the hold and wait correctly and you still do not know if the pilot is lit, some older furnaces had a peak hole (observation hole) for viewing the pilot and gas burner. I'm not totally sure about yours, as your picture does not zoom in close enough on the gas burner. Some gas systems have a glass sight glass hole you can look through; yours most likely does not, but it may have a teardrop cover that flips open to expose a viewing hole. A small screw holds the tear drop cover, loosen it, swing the cover open, look and see. Then, when all is working, you put the cover back on.
See the red circle on your pic; if you have one, that observation hole would be inside the circle.
Here is a snapshot of where it might be; again, I'm not sure your has it.
As I said before, sometimes the pilot gas line or orifices in the gas valve have crud blocking the gas flow, the pilot valve is not working, the thermocouple no longer works, or the igniter has issues. I'll see if the whole gas valve is even offered for sale anymore and report back later on that.
You asked about the gas pressure. Yes, low gas pressure can make all this worse on a pilot system. The furnace needs an 11" water column (WC) to work properly. This is less than 0.5 psi; it's not a lot. And you do not want a lot above 14" WC, as that creates other issues. Out on the trailer tongue, where the LP tank is, a two-stage gas regulator should set the gas pressure for all the gas appliances in the camper. That regulator could be off setpoint or not working correctly. And yes, the stove burner may light, as even on low gas pressure they can light, but the oven which uses a gas pilot may not work.
I'll caution again and give this friendly advice: Anyone buying a used camper should have the gas system checked for leaks, the appliances checked out, and the main tank regulator ensured to be working correctly before they use it. It's also a good idea to have an annual propane check, or at least one every other year. An LP service or RV tech can perform three checks for you.
https://www.sunlineclub.com/forums/f71/annual-propane-system-checks-10981.html
As a side note, RV gas valves are built cheaply and are not serviceable; they just get replaced. RV gas systems do work, but they are not as good as home or commercial gas valves, etc., that can work well for years and years.
On older campers, every time I do an LP gas check, there is a 50/50 chance I will find something not in spec. The main tank regulator goes bad, and the water heater gas valve leaks. On the WH, the gas valve being so close to the outside that it corrodes more easily.
Hope this helps.
John