Old 01-26-2019, 05:27 PM   #41
Senior Member
 
Join Date: Apr 2011
Location: Maine
Posts: 3,357
SUN #2097
mainah is an unknown quantity at this point
Quote:
Originally Posted by Tinstaafl View Post
I'm quite familiar with the different types of breakers; I do residential construction/remodeling, including all of the electrical work involved. Wire nuts are completely acceptable in situations like this per the NEC. Applied properly, they make an excellent connection.

I do agree that two wires in a single-conductor breaker is a bad idea, even if it was legal (which it's not).
NEC 2008
110.14 Electrical Connections.
__________________

__________________
mainah is offline   Reply With Quote
Old 01-26-2019, 05:56 PM   #42
Senior Member
 
Join Date: Apr 2011
Location: Maine
Posts: 3,357
SUN #2097
mainah is an unknown quantity at this point
Quote:
Originally Posted by Thomascine View Post
Here are pics of the electrical panel. It looks like one breaker is installed with both the 15 amp for the converter and electrical outlets and the 20 amp for the AC.

Thanks for all of the input.

Tommie
The breakers appear to be Siemans so here is where a tandem breaker comes in. Replace the 20 amp breaker with a tandem. Land the existing AC wire on one and the new one on the other pole of the tandem breaker. Yes you are correct on the useage the 15 is for the outlets the 20 is the AC. So before you head off to the store remove the old 20 amp and take it with you to match it up to a tandem then you can give the old one away as a birthday present or something. There are other ways to do this but let's make it real simple with a tandem breaker.
__________________

__________________
mainah is offline   Reply With Quote
Old 01-26-2019, 06:14 PM   #43
Senior Member
 
Join Date: Apr 2011
Location: Maine
Posts: 3,357
SUN #2097
mainah is an unknown quantity at this point
Quote:
Originally Posted by enormiss View Post
Looks like you can add a jumper and another breaker for your heater outlet install
Yes he could jumper L1 L2 and add a breaker but the knockout is for a double pole breaker so a blank plate and another breaker would be required. Every so often you find motorhomes with a back feed 30 single pole that actually fills a two breaker slot that is used as a main breaker.
__________________
mainah is offline   Reply With Quote
Old 01-26-2019, 07:59 PM   #44
Moderator
 
JohnB's Avatar
 
Join Date: Nov 2006
Location: Ohio
Posts: 12,654
SUN #89
JohnB is on a distinguished road
Tommie,

As an option, and if your shore power cord hole will allow, buy a 25 ft, no. 12 AWG (20 amp) extension cord. Many power posts have both the 30 amp receptacle and a 20 amp receptacle next to it. Plug in the extension cord to the power post and feed the end of it into the camper through the shore line cord hole. Then plug the heater into the extension cord. This requires no wiring.

Hope this helps

John
__________________
Current Sunlines: 2004 T310SR, 2004 T1950, 2004 T2475, 2007 T2499, 2004 T317SR
Prior Sunlines: 2004 T2499 - Fern Blue
2005 Ford F350 Lariat, 6.8L V10 W/ 4.10 rear axle, CC, Short Bed, SRW. Reese HP trunnion bar hitch W/ HP DC

Google Custom Search For Sunline Owners Club
JohnB is offline   Reply With Quote
Old 01-26-2019, 09:28 PM   #45
Senior Member
 
Tinstaafl's Avatar
 
Join Date: Nov 2018
Location: Pennsylvania
Posts: 328
SUN #10986
Tinstaafl is an unknown quantity at this point
Quote:
Originally Posted by mainah View Post
NEC 2008
110.14 Electrical Connections.
Not sure where that supports your point, or exactly what that point is.

Nevertheless, this is hardly the venue for abstruse discussion and interpretation of electrical codes. I'll let it rest.
__________________
Tinstaafl is offline   Reply With Quote
Old 01-27-2019, 01:10 AM   #46
Senior Member
 
Thomascine's Avatar
 
Join Date: Sep 2016
Location: Virginia
Posts: 814
SUN #8893
Thomascine is an unknown quantity at this point
Quote:
Originally Posted by JohnB View Post
Tommie,

As an option, and if your shore power cord hole will allow, buy a 25 ft, no. 12 AWG (20 amp) extension cord. Many power posts have both the 30 amp receptacle and a 20 amp receptacle next to it. Plug in the extension cord to the power post and feed the end of it into the camper through the shore line cord hole. Then plug the heater into the extension cord. This requires no wiring.

Hope this helps

John
Hi JohnB. I remember this from one of your posts and I did copy it. However, I had the heater plugged into the extension cord and the cord still got really hot. I'm going to have to pull the cord and toss it and maybe the heater as well. It's possible that maybe one or both are faulty. Just trying to be safe. I have another 12 AWG cord I can run. The 12 AWG cords are pretty thick so it's not easy to pull through the small space with the 30 amp cord. And the outside shore line hole cover does not close with both cords in place. Trying to keep mice out. This has been a bad year for us with mice. This is why I was considering the dedicated outlet. But I will give the extension cord solution another try.

Thanks everyone for the options.
__________________
Thomascine is offline   Reply With Quote
Old 01-27-2019, 07:16 AM   #47
Senior Member
 
Join Date: Apr 2011
Location: Maine
Posts: 3,357
SUN #2097
mainah is an unknown quantity at this point
Tommie I just enlarged your picture of the load center, what you have there is a tandem breaker all ready. The box will except two breakers, either two tandems or two singles or a combination the caviant is L1 and L2 would have to be Jumpered in order for it to work. I know this is sounding a bit complex and it's too bad you are 700 miles away it's something that could be done in less that a half an hour.
__________________
mainah is offline   Reply With Quote
Old 01-27-2019, 04:23 PM   #48
Senior Member
 
Thomascine's Avatar
 
Join Date: Sep 2016
Location: Virginia
Posts: 814
SUN #8893
Thomascine is an unknown quantity at this point
Quote:
Originally Posted by mainah View Post
Tommie I just enlarged your picture of the load center, what you have there is a tandem breaker all ready. The box will except two breakers, either two tandems or two singles or a combination the caviant is L1 and L2 would have to be Jumpered in order for it to work. I know this is sounding a bit complex and it's too bad you are 700 miles away it's something that could be done in less that a half an hour.
Thanks Mainah. I thought it looked like one breaker but I haven't had time to go back and look again. I know a guy who is familiar but I am not going to bother him with it unless for some reason the new extension cord and different heater does not solve my problem.

Thanks again.

Tommie
__________________
Thomascine is offline   Reply With Quote
Old 01-28-2019, 07:11 AM   #49
Senior Member
 
Join Date: Apr 2011
Location: Maine
Posts: 3,357
SUN #2097
mainah is an unknown quantity at this point
I actually did exactly what you are trying to do in my camper before I made the "central electric heating"system to run a floor heater so I have an outlet under the seat now. I have 4 separate circuits in my panel. Having bits and pieces at my disposal makes life a bit easier. Here is something I looked at awhile back no fan no noise and minimum current draw. https://www.eheat.com/envi-high-effi...I-erYjdOQ4AIV2
__________________
mainah is offline   Reply With Quote
Old 01-28-2019, 06:36 PM   #50
Senior Member
 
Thomascine's Avatar
 
Join Date: Sep 2016
Location: Virginia
Posts: 814
SUN #8893
Thomascine is an unknown quantity at this point
Quote:
Originally Posted by mainah View Post
...Here is something I looked at awhile back no fan no noise and minimum current draw. https://www.eheat.com/envi-high-effi...I-erYjdOQ4AIV2
Thanks Mainah. I will take a look at that heater.

I think I am still wanting to install a dedicated outlet. I am in the process of getting everything needed. With that said, what can I use to jumper the A and B circuits? I have replaced breakers before but never done anything with jumpers.

Thanks,
Tommie
__________________
Thomascine is offline   Reply With Quote
Old 01-29-2019, 06:14 AM   #51
Senior Member
 
Join Date: Apr 2011
Location: Maine
Posts: 3,357
SUN #2097
mainah is an unknown quantity at this point
A short piece of #10 wire is all you need there are two screws at the top of the load center one already has a wire connected to it the other does not so it needs to go across to the other lug. The box is a 240/120 box they did not install a jumper and left it up to the installer to decide what voltage was to be used. The jumper will power both lugs as 120 volts this will power the stab in for your second breaker otherwise it would just be decorative. It's -5 this morning if it warms up to + something I'll see if I can get a picture for you.
__________________
mainah is offline   Reply With Quote
Old 01-29-2019, 12:35 PM   #52
Senior Member
 
Thomascine's Avatar
 
Join Date: Sep 2016
Location: Virginia
Posts: 814
SUN #8893
Thomascine is an unknown quantity at this point
Quote:
Originally Posted by mainah View Post
A short piece of #10 wire is all you need there are two screws at the top of the load center one already has a wire connected to it the other does not so it needs to go across to the other lug. The box is a 240/120 box they did not install a jumper and left it up to the installer to decide what voltage was to be used. The jumper will power both lugs as 120 volts this will power the stab in for your second breaker otherwise it would just be decorative. It's -5 this morning if it warms up to + something I'll see if I can get a picture for you.
That's what I thought. Thanks a bunch!
__________________
Thomascine is offline   Reply With Quote
Old 03-23-2019, 02:57 PM   #53
Senior Member
 
Thomascine's Avatar
 
Join Date: Sep 2016
Location: Virginia
Posts: 814
SUN #8893
Thomascine is an unknown quantity at this point
Finally! After a lot of cursing, got the 20amp outlet installed. Not a lot of room to work with. Now just gotta secure the wiring and then finish up the dual propane setup and I will be all set, at least for now. Thanks a bunch for all of the advice and direction. Much appreciated!

Tommie
Attached Images
File Type: jpg IMG_3552.jpg (88.5 KB, 12 views)
File Type: jpg IMG_3555.jpg (49.4 KB, 7 views)
File Type: jpg IMG_3556.jpg (68.5 KB, 8 views)
File Type: jpg IMG_3557.jpg (61.6 KB, 7 views)
__________________

__________________
Thomascine is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Winter Camping... in May!? henryj Sunline Community 5 06-10-2009 04:50 PM
Winter Camping WandaLust Sunline Community 11 11-21-2008 07:23 PM
Your Winter Camping Fix emam Sunline Community 11 02-03-2008 03:52 PM
Winter Rally for the GA'RVers camping group partimcmpr Sunline Owners Meet & Greet 0 01-21-2008 09:25 PM
Winter Camping purplesuebug Sunline Community 22 06-29-2007 10:41 AM


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Sunline RV or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 04:00 PM.


×